The heat exchanger is modelled as a volumetric energy source where the energy transfer between two fluid streams is based on an effectiveness, specified as a function of the mass flow rates.
\[ Q_t = e \left(\dot{m}_1 , \dot{m}_2 \right) \left(T_2 - T_1\right) \dot{m}_1 C_p, \]
where:
| \( Q_t \) | = | total heat source |
| \( e(\dot{m}_1,\dot{m}_2) \) | = | effectiveness table |
| \( \dot{m}_1 \) | = | net mass flux entering heat exchanger [kg/s] |
| \( \dot{m}_2 \) | = | secondary mass flow rate [kg/s] |
| \( T_1 \) | = | primary inlet temperature [K] |
| \( T_2 \) | = | secondary inlet temperature [K] |
| \( C_p \) | = | specific heat capacity [J/kg/K] |
The energy source is distributed across the cells according to:
\[ Q_c = \frac{V_c |U_c| (T_c - T_{ref})}{\sum(V_c |U_c| (T_c - T_{ref}))}, \]
where:
| \( Q_c \) | = | energy source for cell |
| \( V_c \) | = | volume of the cell [m3] |
| \( U_c \) | = | local cell velocity [m/s] |
| \( T_c \) | = | local call temperature [K] |
| \( T_{ref} \) | = | min or max(T) in cell zone depending on the sign of \( Q_t \) [K] |
Optional entries:
primaryInletT : sets the primary inlet temperature. If not set, the flux-averaged temperature is usedtargetQdot : the secondary inlet temperature is derived from a target heat rejectionThe option is specified using:
heatExchanger1
type effectivenessHeatExchanger;
selectionMode cellZone;
cellZone porosity;
secondaryMassFlowRate 1.0;
secondaryInletT 336;
faceZone facesZoneInletOriented;
outOfBounds clamp;
file "effTable";
// Optional
// primaryInletT 293;
// targetQdot 1500;
The two-dimensional effectiveness table is specified according to, e.g. for the table
| mfr2,1 | mfr2,2 | mfr2,3 | |
| mfr1,1 | A | B | C |
| mfr1,2 | D | E | F |
| mfr1,3 | G | H | I |
the equivalent entry becomes:
mfr1,1
(mfr2,1 A)
(mfr2,2 B)
(mfr2,3 C)
mfr1,2
(mfr2,1 D)
(mfr2,2 E)
(mfr2,3 F)
mfr1,3
(mfr2,1 G)
(mfr2,2 H)
(mfr2,3 I)
Tutorials
Source code
Copyright © 2018 OpenCFD Ltd.